Thermal-Magnetic Circuit Breakers 3600/3900
Single pole thermal-magnetic circuit breaker with tease-free, trip-free,
snap action mechanism and two button operation (M-type TM CBE to
EN 60934). Designed for plug-in mounting with E-T-A sockets 17-P10-Si,
23-P10-Si, 63-P10-Si; or panel mounting using E-T-A clips. Featuring
an unprotected shunt tap terminal and optional auxiliary contacts. Type
3900 offers lower internal resistance values and is fitted as standard
with auxiliary contacts and an intermediate reset position in which all
contacts are isolated.
Approved to CBE standard EN 60934 (IEC 60934).
Typical applications
Process control systems, instrumentation, communications systems,
rail vehicles.
3600
standard type
3900
low-resistance type
Ordering information
Type No.
3600
standard version with shunt tap terminal -3
3900
low-resistance version
Terminal design
P10
blade terminals 6.3-0.8 (QC .250)
Auxiliary contacts (3900: intermediate position as standard)
Si
with blade terminals 6.3-08,one each NO/NC,
Si60
special auxiliary contact (only 3900)
1 NO, closed in the intermediate and ON position
ZR-Si
auxiliary contacts with intermediate position (only 3600)
ZR-Si60
special auxiliary contact (only 3600)
Si3-R
special auxiliary contacts, 2 NC contacts with reset
button (not approved)
Current ratings
0.05...16 A
(type 3600)
0.05...10 A
(type 3900)
3600 - P10 - Si -
10 A
ordering example
Technical data
For further details please see chapter: Technical Information
Voltage rating
AC 240 V, 50/60 Hz; DC 65 V
(UL: AC 250 V; DC 65 V)
Current rating range
3600: 0.05...16 A
3900: 0.05...10 A
Auxiliary circuit
1 A, AC 240 V / DC 65 V
Typical life
5,000 operations at 1 x I
, inductive
5,000 operations at 2 x I
, resistive
Ambient temperature
-30...+60 °C (-22...+140 °F)
Insulation co-ordination
rated impulse
pollution
(IEC 60664 and 60664 A) withstand voltage
degree
2.5 kV
reinforced insulation in operating area
Dielectric strength
(IEC 60664 and 60664A) test voltage
operating area
AC 3,000 V
main/aux. circuit
AC 1,500 V
aux. circuit 4-5/6-7
AC 840 V
Insulation resistance
>100 MΩ (DC 500 V)
Interrupting capacity I
cn
3600
3900
0.05...0.8 A 0.05...0.2 A self-limiting
1...2 A
0.3...2 A
200 A
2.5...16 A
2.5...10 A
400 A
U
(UL 1077)
0.05...16 A
AC 250 V
1,000 A
type 3600: 0.05...16 A
DC 80 V
1,000 A
Degree of protection
operating area IP40
(IEC 60529/DIN 40050)
terminal area IP00
Vibration
5 g (57-500 Hz), ± 0.38 mm (10-57 Hz)
to IEC 60068-2-6, test Fc
10 frequency cycles/axis
Shock
25 g (11 ms) to IEC 60068-2-27, test Ea
Corrosion
96 hours at 5 % salt mist
to IEC 60068-2-11, test Ka
Humidity
240 hours at 95 % RH
to IEC 60068-2-3, test Ca
Mass
approx. 45 g
The exact part number required can be built up from the table of choices shown
above. Ordering references for optional features should be omitted if not required.
Standard current ratings and typical internal resistance values
Current
rating (A)
Internal resistance (Ω)
3600
3900
Current
rating (A)
3600
3900
0.05
0.1
0.2
0.3
0.4
0.8
447
131
10.4
7.1
4.3
1.67
0.61
0.38
0.24
211
48
12.4
5.4
3.1
2.0
1.32
0.76
0.49
0.21
0.101
0.078
0.090
0.061
0.041
0.034
≤ 0.02
≤ 0.02
≤ 0.02
≤ 0.02
≤ 0.02
≤ 0.02
0.054
0.035
0.025
≤ 0.02
≤ 0.02
≤ 0.02
≤ 0.02
Approvals
Authority
3600:
VDE (EN 60934)
CSA/UL
UL
3900:
VDE (EN 60934)
Voltage ratings
AC 240 V; DC 65 V
AC 250 V; DC 80 V
DC 65 V
AC 240 V; DC 65 V
Current ratings
0.05...16 A
0.05...16 A
0.05...25 A
0.05...10 A
Issue A
www.e-t-a.com
Dimensions
-P10-Si
OFF
ON
ø11.5
.453
Internal connection diagrams
with shunt terminal (standard)
and auxiliary contacts (-Si) only 3600
line 1
line 1
ø6.5
.256
ø4
.157
ø8.5
.335
51
2.01
I>
3 (from I
=8 A)
I>
3 (from I
=8 A)
19
.748
Switching position with auxiliary contacts and reset button (-Si3-R)
6.8
.268
6 x 6.8 = 40.8
6 x .268 = 1.61
blade terminals
DIN 46244-A6.3-0.8
(QC .250)
OFF position
line 1
line 1
ON position
line 1
current rating in A
1.69
11.5
.453
I>
3 (from I
=8 A)
I>
3 (from I
=8 A)
I>
3 (from I
=8 A)
8.5
.335
-Si3-R
-Si60
-ZR-Si60
-ZR-Si
OFF
ON
ø11.5
.453
Switching position with special auxiliary contact (-Si60, -ZR-Si60)
ø6.5
.256
ø4
.157
ø8.5
.335
OFF position
line 1
line 1
ON position
line 1
51
2.01
I>
3 (from I
=8 A)
I>
3 (from I
=8 A)
I>
3 (from I
=8 A)
19
.748
6.8
.268
6 x 6.8 = 40.8
6 x .268 = 1.61
current rating in A
1.69
11.5
.453
Switching position with intermediate position and auxiliary
contacts (3600: -ZR-Si, 3900: -Si)
blade terminals
DIN 46244-A6.3-0.8
(QC .250)
OFF position
line 1
line 1
ON position
line 1
I>
3 (from I
=8 A)
I>
3 (from I
=8 A)
I>
3 (from I
=8 A)
8.5
.335
Intermediate position: Holding down reset button and actuating
manual release simultaneously.
Installation drawing
operating area
(reinforced insulation)
Terminal design -P10
mounting area
12.5
.492
38
1.50
This is a metric design and millimeter dimensions take precedence ( mm )
inch
www.e-t-a.com
Issue A
Typical time/current characteristics
3600 0.05 … 7 A
10000
AC
1)
3600 8 … 16 A
10000
AC
1)
3900 0.05 … 10 A
10000
DC
2)
Trip time in seconds
0.1
0.1
0.01
0.01
0.01
0.001
… times rated current
+23 °C
+73.4 °F
-30 °C
-22 °F
0.001
0.001
+60 °C
+140 °F
1)
2)
Magnetic tripping currents are increased by 20% on DC supplies.
Magnetic tripping currents are decreased by 20% on AC supplies.
The time/current characteristic curve depends on the ambient temperature
prevailing. In order to eliminate nuisance tripping, please multiply the circuit
breaker current ratings by the derating factor shown below. See also
section 9 – Technical information.
Ambient temperature °F -22 -4
+14 +32 +73.4 +104 +122 +140
°C -30 -20 -10 0
+23 +40 +50 +60
Derating factor
0.76 0.79 0.83 0.88 1
1.08 1.16 1.24
Accessories
Module 17plus
Modular power distribution system for circuit breakers 2210-S,
3600 or 3900.
For technical details see product group 7.
19" Rack 19BGT2 2U
for 18, 24 or 30 circuits.
For technical data see product group 7.
19" Rack
accommodating up to 30 E-T-A thermal-magnetic circuit breakers
type 3600-P10-Si or 3900-P10-Si.
Issue A
www.e-t-a.com
Accessories
Sockets
17-P10-Si
17-P10-Si-20025
(up to 16 A max. load)
mounted with adapter
Retaining clip Y 300 581 11 to special order.
slot fitting labels from
Phoenix, Weidmüller
polarized blade terminal
DIN 46244-A6.3-0.8 (QC .250)
retaining clip
Bus bar (10-way)
(supplied as a complete package)
for socket 17
(for max. 100 A continuous load)
X 211 157 01 with terminal
X 211 157 02 without terminal
(more positions available on request)
Phoenix terminal AKG 35
max.cross section 35 mm
(AWG 2)
cylinder head screw washer
M4x4 ISO1207
A 4.3 DIN 125
nickel plated
nickel plated
-P10
6.3
depth .248
10 mm
(.394 in.)
2(k)
8.5
.335
2(k)
female
connector
25.8
1.02
41.3
1.63
1.4
.055
23
45.8
1.80
2(i)
33.3
1.31
2(i)
M4 Cu rail, tin-plated
6.5
.256
12.5
.492
symmetrical rail
EN 50022-35x7.5
adapter X20040901
G-profile
EN 50035-G32
12.8
.504
polarization recess
154.8
6.09
Sockets
17-P70-Si
17-P70-Si-20025
Phoenix, Weidmüller
blade terminal DIN 46244 part 2
C profile (2xA2.8-0.8) (QC 2x.110)
retaining clip
Insulate sleeving for bus bar
Y 303 824 01
17
.669
5.4
.213
125
4.92
-P70
2.8
depth .110
10 mm
(.394 in.)
2(k)
2(i)
2(k)
2(i)
Connector bus links -P10
X 210 588 01/
1.5 mm
(AWG 16), brown up to 13 A max. load
X 210 588 02/
2.5 mm
(AWG 14), black up to 20 A max. load
X 210 588 03/
2.5 mm
(AWG 14), red up to 20 A max. load
X 210 588 04/
2.5 mm
(AWG 14), blue up to 20 A max. load
45.8
1.80
100 quick-connect tabs 6.3 (.250)
DIN 46247 tinned brass,
insulated
25.8
1.02
8.5
.335
33.3
1.31
41.3
1.63
1.4
.055
6.5
.256
12.5
.492
symmetrical rail
EN 50022-35x7.5
adapter X20040901
G-profile
EN 50035-G32
polarization recess
Sockets
23-P10-Si
63-P10-Si
Retaining clip Y 300 581 03 to special order.
polarized blade terminals
7.4
.291
7.4
.291
retaining
clip
21
.827
Extraction tool
Y 301 398 02
~70
~2.76
56
2.21
22.2
.874
6 x .268 = 1.61 6.8
.268
4.4
.173
12.5
.492
6.25
.246
57.4
2.26
6 x 6.8 = 40.8
Mounting clip
Y 300 504 02
(2 pcs needed per unit)
1.9
.075
7.5
.295
46
1.81
12.5
.492
polarized
recess
4.4
.173
75
2.95
12.5
.492
7.3
.287
60.4
2.38
8.5
.335
inch
All dimensions without tolerances are for reference only. In the interest of improved design,
performance and cost effectiveness the right to make changes in these specifications
without notice is reserved.Product markings may not be exactly as the ordering codes.
Errors and omissions excepted.
M4
16.5
.650
www.e-t-a.com
12.5
.492
57.4
2.26
64
2.52
64
2.52
Installation drawing with
mounting clips Y 300 504 02
3.5
.138
pressure-relief joint
(1.1 mm (.043 in.)
thick constriction)
Issue A