SmartSlice
The smartest modular I/O system
OMRON's SmartSlice I/O system is compact, intelligent and
easy. When used with OMRON's CS1/CJ1 DeviceNet or
CompoNet master units, no configuration tool is required.
By using built-in functions such as pre-scaling, totalising,
differentiation and alarming in analog I/O units, PLC pro-
gramming can be minimised. Preventive maintenance data
collected by all I/O units can be accessed using CX-Integra-
tor or NS-series Smart Active Parts.
• Most compact in the market (84 mm high)
• Easy set-up, backup and restore functions
• Diagnostics and preventive maintenance data at I/O level
• Detachable terminal blocks allow hot-swapping without
re-wiring
• 3-wire I/O connection with 'push-in' technology, no screw-
driver required
System Configuration
NJ
series
Controller,
CS/CJ PLC
series
or
Trajexia Motion Controller
CX-One for setup,
monitoring and operation
of all OMRON Devices
PLC
Slave
Communication Unit
GRT1-TBR Right Turnback Unit
GCN2-100 Turnback Cable (1 m)
Max. 2 per
station.
I/O Units
GRT1-END End Unit
GRT1-TBL Left Turnback Unit
Up to 64 I/O Units can
be
connected to
a
Communication Unit.
SmartSlice
General Specifications
Common SmartSlice Specifications
Unit power supply voltage
24 VDC (20.4 to 26.4 VDC)
I/O power supply voltage
I/O connection
Screwless push-in technology
Noise immunity
Conforms to IEC61000-4-4, 2.0 kV (power supply line)
Vibration resistance
10 to 60 Hz: 0.7 mm double amplitude 60 to 150 Hz: 50 m/s
Shock resistance
150 m/s
, 3 times in each direction
Dielectric strength
500 VAC (between isolated circuits)
Insulation resistance
20 M min. (between isolated circuits)
Ambient operating temperature
-10 to 55°C (with no icing or condensation)
Ambient operating humidity
25% to 85%
Operating environment
No corrosive gases
Ambient storage temperature
-25 to 65°C (with no icing or condensation)
Mounting
35 mm DIN rail
Communication Units
Model name
Network Specification
GRT1-PNT
PROFINET-IO
GRT1-PRT
PROFIBUS-DPV1
GRT1-DRT
DeviceNet
GRT1-CRT
CompoNet
GRT1-ML2
GRT1-ECT
MECHATROLINK-II EtherCAT for
for Trajexia
Trajexia and
Sysmac (NJ)
2 x ML-II
2 x RJ45
Network connector
Network interface power supply
Number of I/O points
Number of connectable Units
I/O power supply
Status flags
Parameter backup and restore
Open-style
4-pin CompoNet
DeviceNet
connector,
dual screwless
push-in dual
connections.
Internal
External,
Internal
11 to 25 VDC, 22 mA
1,024 inputs and outputs max. (128 bytes each)
32 bytes input +
32 bytes output
max.
64 SmartSlice I/O Units max.
24 VDC, 4 A max.
1 word for Communications Unit status flags
up to 2 KB of data per I/O Unit.
2 x RJ45, built-in
switch with support
for MRP
redundancy.
9-pin D-Sub
1,024 inputs and
outputs max.
(128 bytes total)
External 24 VDC
(+10% - 15%)
1,024 inputs and
outputs max.
(128 bytes total)
Control System
Digital Input Units
Model name
Signal type
Number of input points
Power terminals
ON voltage
ON current
OFF voltage
OFF current
ON delay / OFF delay
Model name
Signal type
Power terminals
Input voltage
ON voltage
ON current
OFF voltage
OFF current
GRT1-ID4
GRT1-ID4-1
DC input (for sinking out- DC input (for sourcing
puts, NPN type)
outputs, PNP type)
4 inputs
4 x V (24 V) + 4 x G (0 V)
15 VDC min.
6 mA max./point (at 24 VDC)
5 VDC max.
1 mA max.
1.5 ms max.
GRT1-IA4-1
AC input, 110 V
4 inputs
None
100 to 120 VAC
-15% to +10%, 50/60 Hz
70 VAC min.
4 mA min.
20 VAC max.
2 mA max.
10 ms max./55 ms max.
GRT1-IA4-2
AC input, 230 V
GRT1-ID8
puts, NPN type)
8 inputs
4 x G (0 V)
GRT1-ID8-1
outputs, PNP type)
4 x V (24 V)
4 mA max./point (at 24 VDC)
200 to 240 VAC
120 VAC min.
10 ms max./40 ms max.
GRT1-ID4 (NPN)
GRT1-ID4 -1 (PNP)
2-wire sensor
(such as a limit switch)
Signal
24 V
0V
3-wire sensor
with NPN output
(photoelectric or
proximity sensor)
2-wire sensor
Signal
24 V
0V
3-wire sensor with NPN output
(photoelectric or proximity sensor)
GRT1-IA4-1/GRT1-IA4-2
0A
0B
0B
2A
2B
2B
1A
1B
1B
3A
3B
3B
0A
0B
0B
2A
2B
2B
1A
1B
1B
3A
3B
3B
0A
0B
0B
2A
2B
2B
1A
1B
1B
3A
3B
3B
No common signal for inputs.
Common signal for four inputs.
GRT1-ID8 (NPN)
GRT1-PD8
External
24-V I/O
power
supply
3-wire sensor
Signal
24 V
0V
3-wire sensor
Signal
24 V
0V
GRT1-ID8-1 (PNP)
GRT1-ID8
GRT1-PC8-1
3-wire sensor
Signal
24 V
0V
3-wire sensor
Signal
24 V
0V
GRT1-ID8-1
Signal
24 V
2-wire switch
2-wire switch
Signal
24 V
0V
0V
3-wire sensor
3-wire sensor
SmartSlice
Digital Output Units
Model name
Signal type
Number of output points
Power terminals
Rated voltage
GRT1-OD4
GRT1-OD4-1
Transistor output
Transistor output
(NPN type, sinking)
(PNP type, sourcing)
4 outputs
4 x V (24 V)
4 x G (0 V)
GRT1-OD4G-1
GRT1-OD4G-3
Transistor output
(PNP type, sourcing), with short-circuit protection
24 V I/O power supply
via the front terminal of
the unit.
from 4 x 2.0 A at 30 °C
to 4 x 1.0 A at 55 °C
1.2 VDC max. (at 2 A)
Rated output current
Residual voltage
Leakage cuurent
ON delay / Off delay
Model name
Signal type
500 mA max./point
1.2 VDC max. (at 500 mA)
0.1 mA max.
0.5 / 1.5 ms max.
GRT1-OD8
Transistor output
(NPN type, sinking)
GRT1-OD8-1
Transistor output
Power terminals
Rated voltage
Residual voltage
Leakage cuurent
Mechanical life expectancy
Electrical life expectancy
8 outputs
4 x V (24 V)
4 x G (0 V)
500 mA max./point
0.1 mA max.
0.5 / 1.5 ms max.
GRT1-OD8G-1
GRT1-ROS2
Transistor output
Relay output
(normally open)
with short-circuit protec-
tion
2 outputs (with 2 termi-
nals per connection)
n.a.
250 VAC / 24 VDC
2 A (min. 1 mA @ 5 VDC)
15 ms max.
20,000,000 times min.
100,000 times min.
GRT1-OD4
NC
NC
NC
NC
Solenoid,
valve, etc.
GRT1-OD4-1
NC
NC
NC
NC
Solenoid,
valve, etc.
GRT1-OD4G-1 (PNP)
3-wire
actuator
Solenoid,
valve, etc.
3-wire
actuator
GRT1-PC8-1
Solenoid,
valve, etc.
3-wire
actuator
GRT1-OD8 (NPN)
GRT1-OD8
24 VDC
GRT1-OD4G-3 (PNP)
Solenoid,
valve, etc.
3-wire
actucator
3-wire
actuator
Control System
GRT1-PC8
3-wire
actuator
3-wire
actuator
GRT1-OD8(G)-1 (PNP)
GRT1-OD8-1
GRT1-ROS2
AC power supply
(or DC power supply)
C0
NC
C1
NC
C0
NC
C1
NC
Load
AC power supply
Load
Solenoid,
valve, etc.
3-wire
actuator
Pulse I/O Units
Model name
Counter input
GRT1-CT1
A/B incremental
encoder,
or pulse/direction,
or pulse up/down
24 VDC, NPN type
GRT1-CT1-1
A/B incremental
encoder,
or pulse/direction,
or pulse up/down
24 VDC, PNP type
GRT1-CP1-L
A/B/Z incremental
encoder,
or pulse/direction/reset
24 VDC, PNP type, or
RS422 Line driver levels
100 kHz
Counter signal type
Max. frequency
Counter range
Comparison values
Control Input
Control Input functions
Control Outputs
Control Output functions
Additional functions
60 kHz
32 bit double signed integer
1 range (2 comparison values)
2 independent ranges
IN0, DC input (NPN type) IN0, DC input (PNP type)
Capture, Preset, Reset
Capture, Preset, Reset,
Z enable
OUT0, Transistor Output OUT0, Transistor Output OUT0, OUT1, Transistor
(NPN, sinking)
(PNP, sourcing)
Output (PNP, sourcing)
Range comparison, manual override
On-the-fly reconfiguration, Frequency measurement
Note: Pulse I/O Units are not supported by GRT1-ML2 and GRT1-ECT.
GRT1-CT1(-1)
GRT1-CT1 (NPN)
Z/IN
N.C.
OUT
N.C.
N.C.
GRT1-CT1-1 (PNP)
Z/IN
N.C.
OUT
N.C.
N.C.
GRT1-CP1-L
24-V rotary encoder
(all DIP switch pins ON)
IN
N.C.
N.C.
N.C.
OUT0
OUT1
Line driver rotary encoder
(all DIP switch pins OFF)
A+
B+
Z+
IN
A–
B–
Z–
OUT0
OUT1
SmartSlice