SEC/S Stella Song
Approved
Ericsson Internal
TABLE OF CONTENTS
No.
1 (2)
Prepared (also subject responsible if other)
BMR463 series
PoL Regulators
Input
4.5-14
V, Output up to
A /
66
Key Features
Checked
Date
001 52-EN/LZT 146 434 Uen
Specification
Technical
EN/LZT 146
434
R3A
Sept
2012
© Ericsson AB
Rev
Reference
2012-09-26
Small package
25.65 x 13.8 x 8.2 mm (1.01 x 0.543 x 0.323 in)
SIP: 26.3 x 7.6 x 15.6 mm (1.035 x 0.30 x 0.614 in)
0.6 V - 3.3 V output voltage range
High efficiency, typ. 97.1% at 5Vin, 3.3Vout half load
Configuration and Monitoring via PMBus
Synchonization & phase spreading
Current sharing, Voltage Tracking & Voltage margining
MTBF 20.2 Mh
Fully regulated
For narrow board pitch applications (15 mm/0.6 in)
Non-Linear Response for reduction of decoupling cap.
Input under voltage shutdown
Over temperature protection
Output short-circuit &
Output over voltage
protection
Remote Control & Power Good
Voltage setting via pin-strap or PMBus
Advanced Configurable via Graphical
Used Interface
ISO 9001/14001 certified supplier
Highly automated manufacturing ensures quality
General Characteristics
Safety Approvals
Design for Environment
Meets requirements in high-
temperature lead-free soldering
processes.
Contents
Ordering Information
General Information
Safety Specification
Absolute Maximum Ratings
Electrical Specification
20A/ 0.6-3.3V Lay Down version and Power Good option
............................................................. 2
............................................................. 3
............................................................. 4
20A/ 0.6-3.3V Single in Line version (SIP)
EMC Specification
Operating Information
Thermal Consideration
Connections
Mechanical Information
Soldering Information
Delivery Information
Product Qualification Specification
BMR4630002 (TH)
BMR4631002 (SMD)
BMR4630006 (TH)
BMR4631006 (SMD) ............................ 5
BMR4632002...................................... 14
........................................................... 23
........................................................... 33
........................................................... 34
........................................................... 44
........................................................... 47
........................................................... 48
........................................................... 50
Technical Specification
BMR463 series
PoL Regulators
Input
4.5-14
V, Output up to
A /
66
Product program
BMR 463
Output
0.6-3.3 V, 20 A/ 66 W
EN/LZT 146
434
R3A
Sept
2012
© Ericsson AB
Compatibility with RoHS requirements
The products are compatible with the relevant clauses and
requirements of the RoHS directive 2002/95/EC and have a
maximum concentration value of 0.1% by weight in
homogeneous materials for lead, mercury, hexavalent
chromium, PBB and PBDE and of 0.01% by weight in
homogeneous materials for cadmium.
Exemptions in the RoHS directive utilized in Ericsson
Power Modules products are found in the Statement of
Compliance document.
Ericsson Power Modules fulfills and will continuously fulfill
all its obligations under regulation (EC) No 1907/2006
concerning the registration, evaluation, authorization and
restriction of chemicals (REACH) as they enter into force
and is through product materials declarations preparing for
the obligations to communicate information on substances
in the products.
Quality Statement
The products are designed and manufactured in an
industrial environment where quality systems and methods
like ISO 9000, Six Sigma, and SPC are intensively in use to
boost the continuous improvements strategy. Infant
mortality or early failures in the products are screened out
and they are subjected to an ATE-based final test.
Conservative design rules, design reviews and product
qualifications, plus the high competence of an engaged
work force, contribute to the high quality of our products.
Warranty
Warranty period and conditions are defined in Ericsson
Power Modules General Terms and Conditions of Sale.
Limitation of Liability
Ericsson Power Modules does not make any other
warranties, expressed or implied including any warranty of
merchantability or fitness for a particular purpose
(including, but not limited to, use in life support
applications, where malfunctions of product can cause
injury to a person’s health or life).
© Ericsson AB 2012
The information and specifications in this technical
specification is believed to be correct at the time of
publication. However, no liability is accepted for
inaccuracies, printing errors or for any consequences
thereof. Ericsson AB reserves the right to change the
contents of this technical specification at any time without
prior notice.
Product number and Packaging
BMR 463 n
n
n
n
/n
n
n
n
Options
n
n
n
n
n
Mounting
Mechanical
Interface
Configuration
Options
n
06
n
n
n
n
002
n
n
n
Through hole mount version (TH)
Surface mount version (SMD)
Single in line (SIP)
Open frame
PMBus and analog pin strap, with
Voltage Tracking Pin (Pin 4A)
PMBus and analog pin strap, with Power
Good Pin (Pin 4A)
Standard configuration
Negative logic
Antistatic tray of 100 products (SIP only)
Antistatic tape & reel of 200 products
(Sample delivery avalable in lower
quantities. Not for SIP)
n
n
n
Example: Product number BMR 463 0002/001C equals a through-hole
mounted, open frame, PMBus and analog pin strap, voltage tracking pin at
4A, positive RC logic, standard configuration variant, package tape&reel.
General Information
Reliability
The failure rate (
) and mean time between failures
(MTBF= 1/
) is calculated at max output power and an
operating ambient temperature (T
) of +40°C. Ericsson
Power Modules uses Telcordia SR-332 Issue 2 Method 1
to calculate the mean steady-state failure rate and
standard deviation (
Telcordia SR-332 Issue 2 also provides techniques to
estimate the upper confidence levels of failure rates based
on the mean and standard deviation.
Mean steady-state failure rate,
49 nFailures/h
Std. deviation,
12.4 nFailures/h
MTBF (mean value) for the BMR 464 series = 20.2 Mh.
MTBF at 90% confidence level = 15.3 Mh
BMR463 series
PoL Regulators
Input
4.5-14
V, Output up to
A /
66
General information
Ericsson Power Modules DC/DC converters and DC/DC
regulators are designed in accordance with safety
standards IEC/EN/UL 60950-1
Safety of Information
Technology Equipment.
IEC/EN/UL 60950-1 contains requirements to prevent injury
or damage due to the following hazards:
Electrical shock
Energy hazards
Fire
Mechanical and heat hazards
Radiation hazards
Chemical hazards
EN/LZT 146
434
R3A
Sept
2012
© Ericsson AB
Isolated DC/DC converters
It is recommended that a slow blow fuse is to be used at
the input of each DC/DC converter. If an input filter is used
in the circuit the fuse should be placed in front of the input
filter.
In the rare event of a component problem that imposes a
short circuit on the input source, this fuse will provide the
following functions:
Isolate the fault from the input power source so as
not to affect the operation of other parts of the
system.
Protect the distribution wiring from excessive
current and power loss thus preventing hazardous
overheating.
On-board DC/DC converters and DC/DC regulators are
defined as component power supplies. As components
they cannot fully comply with the provisions of any safety
requirements without “Conditions of Acceptability”.
Clearance between conductors and between conductive
parts of the component power supply and conductors on
the board in the final product must meet the applicable
safety requirements. Certain conditions of acceptability
apply for component power supplies with limited stand-off
(see Mechanical Information for further information). It is
the responsibility of the installer to ensure that the final
product housing these components complies with the
requirements of all applicable safety standards and
regulations for the final product.
Component power supplies for general use should comply
with the requirements in IEC 60950-1, EN 60950-1 and
UL 60950-1
Safety of Information Technology Equipment.
There are other more product related standards, e.g.
IEEE 802.3
CSMA/CD (Ethernet) Access Method,
and
ETS-300132-2
Power supply interface at the input to
telecommunications equipment, operated by direct current
(dc),
but all of these standards are based on
IEC/EN/UL 60950-1 with regards to safety.
regulators are UL 60950-1 recognized and certified in
accordance with EN 60950-1.
The flammability rating for all construction parts of the
products meet requirements for V-0 class material
according to IEC 60695-11-10,
Fire hazard testing, test
flames
– 50 W horizontal and vertical flame test methods.
The products should be installed in the end-use equipment,
in accordance with the requirements of the ultimate
application. Normally the output of the DC/DC converter is
considered as SELV (Safety Extra Low Voltage) and the
input source must be isolated by minimum Double or
Reinforced Insulation from the primary circuit (AC mains) in
accordance with IEC/EN/UL 60950-1.
The galvanic isolation is verified in an electric strength test.
The test voltage (V
iso
) between input and output is
1500 Vdc or 2250 Vdc (refer to product specification).
24 V DC systems
The input voltage to the DC/DC converter is SELV (Safety
Extra Low Voltage) and the output remains SELV under
normal and abnormal operating conditions.
48 and 60 V DC systems
If the input voltage to the DC/DC converter is 75 Vdc or
less, then the output remains SELV (Safety Extra Low
Voltage) under normal and abnormal operating conditions.
Single fault testing in the input power supply circuit should
be performed with the DC/DC converter connected to
demonstrate that the input voltage does not exceed
75 Vdc.
If the input power source circuit is a DC power system, the
source may be treated as a TNV-2 circuit and testing has
demonstrated compliance with SELV limits in accordance
with IEC/EN/UL60950-1.
Non-isolated DC/DC regulators
The input voltage to the DC/DC regulator is SELV (Safety
BMR463 series
PoL Regulators
Input
4.5-14
V, Output up to
A /
66
Characteristics
P1
Operating temperature (see Thermal Consideration section)
Storage temperature
Input voltage (See Operating Information Section for input and output voltage relations)
CTRL, SA0, SA1, SALERT, SCL, SDA, VSET, SYNC, GCB, PG
-S, PREF, GND
, +S, VTRK
EN/LZT 146
434
R3A
Sept
2012
© Ericsson AB
min
-40
-40
-0.3
-0.3
-0.3
-0.3
typ
max
0.3
6.5
Logic I/O voltage
Ground voltage differential
Analog pin voltage
Stress in excess of Absolute Maximum Ratings may cause permanent damage. Absolute Maximum Ratings, sometimes referred to as no destruction limits, are
normally tested with one parameter at a time exceeding the limits in the Electrical Specification. If exposed to stress above these limits, function and performance
may degrade in an unspecified manner.
Configuration File
This product is designed with a digital control circuit. The control circuit uses a configuration file which determines the functionality and performance of the product.
The Electrical Specification table shows parameter values of functionality and performance with the default configuration file, unless otherwise specified. The default
configuration file is designed to fit most application needs with focus on high efficiency. If different characteristics are required it is possible to change the
configuration file to optimize certain performance characteristics. Note that current sharing operation requires changed configuration file. See application notes
AN307 and AN312 for further information.
In this Technical specification examples are included to show the possibilities with digital control. See Operating Information section for information about trade offs
when optimizing certain key performance characteristics.
Fundamental Circuit Diagram
i
=70
μF
o
=200
μF
BMR463 series
PoL Regulators
Input
4.5-14
V, Output up to
A /
66
EN/LZT 146
434
R3A
Sept
2012
© Ericsson AB
BMR 463 0002, BMR 463 1002, BMR 463 0006, BMR 463 1006
P1
= -30 to +95°C, V
= 4.5 to 14 V, V
> V
+ 1.0 V
Typical values given at: T
P1
= +25°C, V
= 12.0 V, max I
, unless otherwise specified under Conditions.
Default configuration file, 190 10-CDA 102 0175/001.
External C
IN
= 470 µF/10 mΩ, C
OUT
= 470 µF/10 mΩ. See Operating Information section for selection of capacitor types.
Sense pins are connected to the output pins.
Characteristics
Input voltage rise time
Output voltage without pin strap
Output voltage adjustment range
Output voltage adjustment including
margining
Output voltage set-point resolution
Output voltage accuracy
Internal resistance +S/-S to VOUT/GND
Line regulation
= 0.6 V
= 1.0 V
= 1.8 V
= 3.3 V
= 0.6 V
= 1.0 V
= 1.8 V
= 3.3 V
= 0.6 V
= 1.0 V
= 1.8 V
= 3.3 V
0.001
1.26
1.94
3.31
5.89
22
= 0.6 V
= 1.0 V
= 1.8 V
= 3.3 V
= 0.6 V
= 1.0 V
= 1.8 V
= 3.3 V
= 0.6 V
= 1.0 V
= 1.8 V
= 3.3 V
= 0.6 V
= 1.0 V
= 1.8 V
= 3.3 V
= 0.6 V
= 1.0 V
= 1.8 V
= 3.3 V
89.3
92.8
94.8
79.3
86.0
90.7
93.6
3.12
3.25
3.68
4.52
0.56
0.57
0.68
0.99
Including line, load, temp.
See Note 15
Current sharing operation
See Note 16
Conditions
monotonic
1.2
0.60
0.54
±0.025
-1
-2
4.7
3.63
min
typ
max
2.4
V/ms
% V
mV
Load regulation; I
= 0 - 100%
mV
Oac
Output ripple & noise
=470
μ
F (minimum external
capacitance). See Note 12
mVp-p
lim
sc
Output current
Static input current at max I
Current limit threshold
Short circuit
current
RMS, hiccup mode,
See Note 3
See Note 17
= 0.6 V
= 1.0 V
= 1.8 V
= 3.3 V
50% of max I
η
Efficiency
max I
d
Power dissipation at max I
li
Input idling
power
(no load)
Default configuration:
Continues Conduction
Mode, CCM