DataSheet
MCPC Series
Microprocessor based proportional controller / SSR
Ratings from 25A to 90A @ 48-530 VAC
Low-voltage, current, or potentiometer control
Output status indicator
Separate output enable / disable control
0-100% Control Range
For use with resistive loads only
Control Relays
PRODUCT SELECTION
Control Voltage
40-140 VAC
180-280 VAC
330-530 VAC
25 A
MCPC1225
MCPC2425
MCPC4825
50 A
MCPC1250
MCPC2450
MCPC4850
90 A
MCPC1290
MCPC2490
MCPC4890
AVAILABLE OPTIONS
Line Voltage
12:
48-140 Vrms
24:
180-280 Vrms
48:
330-530 Vrms
Analog Control Signal
A:
0-5 VDC
B:
0-7 VDC
C:
0-10 VDC
D:
4-20 mA
E:
Internal Potentiometer
MC
Required for valid part number
PC
24
U
Rated Current
Product Type
25:
25 Amps
PC:
Proportional Controller
50:
50 Amps
90:
90 Amps
OUTPUT SPECIFICATIONS (voltage)
Operating Voltage (47-63Hz) [Vrms]
Transient Overvoltage [Vpk]
Maximum Off-State Leakage Current @ Rated Voltage [mArms]
Minimum Off-State dv/dt @ Maximum Rated Voltage [V/ sec]
(2)
120 A
48-140
240 A
180-280
480 A
300-530
1200
OUTPUT SPECIFICATIONS (current)
Maximum Load Current
(3)
[Arms]
Minimum Load Current [mArms]
Maximum Surge Current (16.6ms) [Apk]
Maximum On-State Voltage Drop @ Rated Current [Vpk]
Thermal Resistance Junction to Case (Rjc) [°C/W]
Maximum I² t for Fusing (8.3 msec) [A²sec]
25 A
1.6
1.02
260
50 A
1.6
0.63
1620
90 A
90
1.6
0.28
6000
FDE-07-01 REV. A
Do not forget to visit us at:
www.crydom.com
Copyright © 2017 Crydom Inc. Specifications subject to change without notice.
DataSheet
INPUT SPECIFICATIONS
Control Voltage Range (VDC)
Input Current Range [mA] [P1]
Nominal Input Impedance [Ohms] [P3]
Control Must Operate Voltage "On"[VDC][P3]
Control Must Release Voltage "Off" [VDC][P3]
Control Input Current [mA][P3]
PLV Range Option A [VDC][P4]
(2)
PLV Range Option B [VDC][P4]
(2)
PLV Range Option C [VDC][P4]
(2)
PLV Range Option D [VDC][P4]
(2)
Nominal Input Impedance Option A,B,C[ohms][P4]
Nominal Input Impedance Option D [ohms][P4]
Control Relays
DC Control
8-32
28-30
30K
5-32
0-4
0-1.25
0.8-5
1-7
2-10
4-20
20K
220
OUTPUT STATUS FUNCTIONS
Conditions
Initial Logic Supply On
Load Voltage Missing / Load Open (w/control disabled)
Load Voltage Missing / Load Open (w/control enabled)
Analog Input < Threshold
Analog Input < Threshold < max
Analog Input > max
LED
Flash Once
Flash Once Intermittenly
Flash Twice Intermittently
Off
Varying Brightness
On, Bright
GENERAL SPECIFICATIONS
Dielectric Strength, Input/Output/Base (50/60Hz)
Minimum Insulation Resistance (@ 500 VDC)
Maximum Capacitance, Input/Output
Ambient Operating Temperature Range
Ambient Storage Temperature Range
Weight (typical)
Encapsulation
Terminals-Power
Terminals-Control
Recommended Terminal Screw Torque Range:
Parameters
4000 V
RMS
Ohm
10 pF
-20 to 80°C
-40 to 125 °C
3.0 oz (86.5g)
Thermally conductive Epoxy
Screws and Saddle Clamps Furnished, Unmounted
Barrier Strip Screw Terminals
8-32 Screws -20 in. lbs.(Screws dry without grase)
GENERAL NOTES
Voltages are reference to GND (Ground = 0 VDC) P2
(2)
PLVI voltage can go up to max. supply voltage without damage
www.crydom.com
DataSheet
MECHANICAL SPECIFICATIONS
Tolerances: ±0.02 in / 0.5 mm
All dimensions are in: inches [millimeters]
Control Relays
Analog Input OPTIONS: A, B, C, D
MOUNTING
HOLE/SLOT
0.19 (4.9) DIA.
1.10
(27.9)
.45
(11.4)
8-32 TERMINAL
(2 PLACES)
MOUNTING
HOLE/SLOT
0.19 (4.9) DIA.
Analog Input OPTIONS: E (Internal Potentiometer)
1.10
(27.9)
.45
(11.4)
8-32 TERMINAL
(2 PLACES)
1/L1
OUTPUT
2/T1
1.88
[47.8]
OUTPUT
STATUS
P4
P3
P2
P1
2.31
[58.8]
1/L1
OUTPUT
2/T1
1.88
[47.8]
OUTPUT
STATUS
P3
P2
P1
2.31
[58.8]
BASE PLATE
.125(3.2)
1.78
(45.3)
.86
(21.8)
BASE PLATE
.125(3.2)
1.78
(45.3)
.86
(21.8)
THERMAL DERATE INFORMATION
25A
50A
1˚C/W
2˚C/W
3˚C/W
110
90A
1˚C/W
1.5˚C/W
.5˚C/W
95
.2˚C/W
Base Plate Temp (˚C)
.5˚C/W
.4˚C/W
Power Dissipation
Power Dissipation
Power Dissipation
2˚C/W
1˚C/W
110
NO HEATSINK
NO HEATSINK
Load Current (Amps)
Max Ambient Temp. (ºC)
Load Current (Amps)
Load Current (Amps)
www.crydom.com
DataSheet
WIRING DIAGRAM
(for Options A, B or C using an external potentiometer)
10k to 50k pot for
Options A, B or C
1/L1
Control Relays
Electrical Connections
AC
OUTPUT
P4
Setpoint Adjust
P1
P4
P2
2/T1
Enable
P1
+Vdc
DC
Supply
OUTPUT
STATUS
10K - 50K
For A,B or C Option
P1
8-32Vdc (+)
P2
Ground (-)
P3
ON/OFF Control
P4
0-5V, 0-7V, 0-10V, 4-20mA
Wiring for Option E
Enable
P1
+Vdc
DC
Supply
Conditions
Initial Logic Suppy On
Analog Input > max
LED
Flash Once
Flash Once Intermittently
Off
Varying Brightness
On, Bright
OUTPUT VS ANALOG INPUT SIGNAL CURVES
0-5Vdc Option A
as a Percentage of Line Voltage
True RMS Output Voltage
Input Voltage P4
50/60Hz
0-7Vdc Option B
50/60Hz
0-10Vdc Option C
50/60Hz
Input Voltage P4
Input Voltage P4
4-20mA Option B
50/60Hz
19
21
Input Voltage P4
AGENCY APPROVALS, CONFORMANCES AND EMC
Agency Approvals
E116949
Rev. 072817
ECN 20288
www.crydom.com
DataSheet
DANGER / PELIGRO / DANGER /GEFAHR / PERICOLO /
危险
HAZARD OF
ELECTRIC
SHOCK,
EXPLOSION,
OR ARC FLASH.
Disconnect all
power before
installing or
working with
this equipment.
Verify all
connections
and replace all
covers before
turning on
power.
Failure to follow
these
instructions will
result in death
or serious injury.
Control Relays
RIESGO DE
DESCARGA
ELECTRICA O
EXPLOSION.
Desconectar
todos los
suministros de
energia a este
equipo antes
de trabajar
con este equipo.
Verificar todas
las conexiones
y colocar todas
las tapas antes
de energizer
el equipo.
El
incumplimiento
de estas
instrucciones
puede provocar
la muerte o
lesiones serias.
RISQUE DE
DESCHARGE
ELECTRIQUE
OU EXPLOSION
Eteindre
toutes les
sources
d'énergie de
cet appareil
avant de
travailler
dessus de cet
appareil
Vérifier tous
connections, et
remettre tous
couverts en
olace avant de
mettre sous
De non-suivi de
ces instructions
provoquera la
mort ou des
lésions sérieuses
sérieuses.
GEFAHR EINES
ELEKTRISCHE
N SCHLAGES
ODER EINER
EXPLOSION.
Stellen Sie
jeglichen
Strom ab, der
dieses Gerät
versorgt, bevor
Sie an dem
Gerät Arbeiten
durchführen
Vor dem
Drehen auf
Energie alle
Anschlüsse
überprüfen
und alle
Abdeckungen
ersetzen.
Unterlassung
dieser
Anweisungen
können zum
Tode oder zu
schweren
Verletzungen
führen.
RISCHIO DI
SCOSSA
ELETTRICA O
DELL’ESPLOSIONE.
Spenga tutta
l'alimentazione
che fornisce
questa
apparecchiatura
prima di lavorare
a questa
apparecchiatura
Verificare tutti
i collegamenti
e sostituire
tutte le coperture
prima
dell’accensione
L'omissione di
queste istruzioni
provocherà la
morte o
lesioni serie
存在电击、
爆炸或电弧
闪烁危险
在操½此设
备之前请先
关闭电源。
若不遵守这些说明,
可½会导致严重的
人身伤害甚至死亡。
WARNING / AVERTISSEMENT / WARNUNG /ADVERTENCIA / AVVERTENZA /
警告
RISK OF MATERIAL DAMAGE AND HOT
ENCLOSURE
The product's side panels may be hot, allow
the product to cool before touching.
Follow proper mounting instructions including
torque values.
Do not allow liquids or foreign objects to enter
this product.
RISQUE DE DOMMAGE MATERIEL ET DE
SURCHAUFFE DU BOITIER
Les panneaux latéraux du produit peuvent être
chauds. Laisser le produit refroidir avant de le
toucher.
Respecter les consignes de montage, et
notamment les couples de serrage.
Ne pas laisser pénétrer de liquide ni de corps
étrangers à l'intérieur du produit.
GEFAHR VON MATERIALSCHÄDEN UND
GEHÄUSEERHITZUNG
Die Seitenwände können heiß sein. Lassen Sie
das Produkt abkühlen, bevor Sie es berühren.
Beachten Sie die Montageanweisungen,
Führen Sie keine Flüssigkeiten oder
Fremdkörper in das Produkt ein.
Le non-respect de cette directive peut entraîner,
Failure to follow these instructions can result in des lésions corporelles graves ou des
serious injury, or equipment damage.
dommages matériels.
Die Nichtbeachtung dieser Anweisung kann
Körperverletzung oder Materialschäden
zur Folge haben.
RIESGO DE DAÑOS MATERIALES Y DE
SOBRECALENTAMIENTO DE LA UNIDAD
Los paneles laterales del producto pueden
estar calientes. Esperar que el producto se
enfríe antes de tocarlo.
Respetar las instrucciones de montaje, y en
particular los pares de apretado.
No dejar que penetren líquidos o cuerpos
extraños en el producto.
Si no se respetan estas precauciones pueden
producirse graves lesiones, daños materiales.
RISCHIO DI DANNI MATERIALI E D'INVOLUCRO
CALDO
I pannelli laterali dell'apparecchio possono
scottare; lasciar quindi raffreddare il prodotto
prima di toccarlo.
Seguire le istruzioni di montaggio corrette.
Non far entrare liquidi o oggetti estranei in questo
apparecchio.
La mancata osservanza di questa precauzione può
causare gravi rischi per l'incolumità personale o
danni alle apparecchiature.
材料损坏和高温外壳的危险性
产品的一侧面板可½很热,在其冷却前请
不要触碰。
遵照正确的安装说明,包括扭矩值。
请勿让液½及其他异物进入本产品。
如不½正确执行这些操½说明,
极有可½造成严重人½伤害或者设备的损坏。
www.crydom.com