Protection Relays & Controls
Generator & Single-Function Protection–Overcurrent
T2200 SERIES
3-Phase Overcurrent Relay
The T2200 Overcurrent Relay is designed for generator
or feeder protection against overcurrent in each of the
three phases.
The T2200 detects the highest of the 3 input currents and, if
this exceeds the preset level (0.5 - 1.4 x I
), the pick-up LED
will indicate and the delay timer will be started. After the
preset time (3-30 sec.) has expired, the output relay and the
corresponding LED will be activated, provided that the current
level was exceeded for the entire delay time.
Features & Benefits
Simplified Circuit Diagram
Accepts high supply
voltage variation
BENEFITS
Ensures correct operation in spite of voltage
supply fluctuations (fulfills marine class
requirement)
Provides quick and concise status information
Simplifies design and installation.
No need for PTs.
Economic solution for tripping non-essential
load, before main breaker trip
Protects the unit against high AC voltage and
currents from the installation including spikes
Easy installation
U
SUPPLY
T2200
(3-Phase Overcurrent Relay)
OVERCURRENT
Visual indication of
power, pick-up, and
output trip
Direct line-line or line-
neutral voltage supply
(up to 690 Vac)
Available with extra
output with instant trip
Galvanic isolated inputs
DIN-rail or screw-mount
& adjustment by
potentiometers
ADDTIONAL
OUTPUT RELAY
L1 L2 L3
Ordering Information
ORDERING
NUMBER
TERMINALS
1-3
2-3
FUNCTION
Trip Level
Delay
Max. Voltage
Voltage Range
Consumption
0.5-1.4 x I
3-30 sec.
660 V
60-110%
Voltage 5 VA at U
Current 0.3 VA at I
Continuous Current
2 x I
Frequency Range
45-400 Hz
Output Relay
Normally de-energized
Contact Rating
AC: 400 V, 5 A, 2000 VA
DC: 150 V, 5 A, 150 W
Overall Accuracy
±5%
Repeatability
±1%
–20°C to + 70°C
Dielectric Test
2500 V, 50 Hz
EMC
CE according to EN50081-1, EN50082-1,
EN50081-2, EN50082-2
Approvals
Certified by major marine classification societies
Burn-in
50 hours before final test
Enclosure Material
Polycarbonate. Flame retardant
Weight
0.5 kg
Dimensions
70 mm (2.76”);
100 mm (3.94”);
115 mm (4.52”)
Installation
35 mm DIN rail or 4 mm (
”) screws
T2200.0010
T2200.0020
T2200.0030
T2200.0040
T2200.0050
T2200.0060
T2200.0070
T2200.0080
T2200.0090
T2200.0100
T2200.0110
450 V
450 V
230 V
230 V
230 V
450 V
110 V
480 V
24 Vdc
450 V
450 V
400 V 5 A Latching output, resetable
energized
400 V 5 A Normally resetable output,
latching,
110 V 5 A Latching output, resetable
1 A Latching output, resetable
Normally energized output,
400 V 5 A latching, resetable, delay 6-60 sec.
100 V 5 A Latching output, resetable
415 V 5 A Latching output, resetable
400 V 5 A Instantly extra output relay
400 V 1 A Instantly extra output relay
Other supply voltages and combinations are available on request.
© 2014 Littelfuse Protection Relays & Controls
Littelfuse.com/t2200
Rev: 4-B-111014