02/11/2015
www.crouzet.com
"Expandable" range with display XD26 Part number 88970165
Green LCD with 4 lines of 18 characters and configurable backlighting
More cost effective solution
Industrial temperature range (-20 °C →+55 °C)
Analogue inputs 0-10 VDC or 0-20 mA/Pt100 with converters
Open to XN network communication extensions and digital I/O or analogue extensions
Part numbers
XD26
Inputs
16 digital (including 6 analogue)
Outputs
10 relays (8 x 8 A relay and 2 x 5 A relay)
Supply
12 V DC
General environment characteristics for CB, CD, XD, XB, XR and XE product types
Certifications
Conformity to standards (with the low voltage directive
and EMC directive)
CE, UL, CSA, GL
IEC/EN 61131-2 (Open equipment)
IEC/EN 61131-2 (Zone B)
IEC/EN 61000-6-2,
IEC/EN 61000-6-3 (*)
IEC/EN 61000-6-4
(*) Except configuration (88 970 1.1 or 88 970 1.2) + (88 970 250 or 88 970 270) + 88 970 241 class A (class B in a metal enclosure)
None
In accordance with IEC/EN 60529 :
IP40 on front panel
IP20 on terminal block
3 in accordance with IEC/EN 60664-1
Degree : 2 in accordance with IEC/EN 61131-2
Operation : 2000 m
Transport : 3,048 m
Immunity to vibrations IEC/EN 60068-2-6, Fc test
Immunity to shock IEC/EN 60068-2-27, Fa test
Immunity to ESD IEC/EN 61000-4-2, level 3
Immunity to radiated electrostatic fields
IEC/EN 61000-4-3,
Immunity to fast transients (burst immunity)
IEC/EN 61000-4-4, level 3
Immunity to shock waves
IEC/EN 61000-4-5
Radio frequency in common mode
IEC/EN 61000-4-6, level 3
Voltage dips and breaks (AC)
IEC/EN 61000-4-11
Immunity to damped oscillatory waves
IEC/EN 61000-4-12
Class B (*) in accordance with EN 55022, EN 55011 (CISPR22, CISPR11) group 1
(*) Except configuration (88 970 1.1 or 88 970 1.2) + (88 970 250 or 88 970 270) + 88 970 241 class A (class B in metallic cabinet)
-20 →+55 °C (+40 °C in a non-ventilated enclosure) in accordance with IEC/EN 60068-2-1 and IEC/EN 60068-2-2
-40 →+70 °C in accordance with IEC/EN 60068-2-1 and IEC/EN 60068-2-2
95 % max. (no condensation or dripping water) in accordance with IEC/EN 60068-2-30
On symmetrical DIN profile, 35 x 7.5 mm and 35 mm x 15 or panel (2 x 4 mm Ø)
Flexible wire with ferrule =
1 conductor : 0.25 to 2.5 mm
(AWG 24...AWG 14)
2 conductors 0.25 to 0.75 mm
(AWG 24...AWG 18)
Semi-rigid wire =
1 conductor : 0.2 to 2.5 mm
(AWG 25...AWG 14)
Rigid wire =
(AWG 25...AWG 14)
2 conductors 0.2 to 1.5 mm
(AWG 25...AWG 16)
Tightening torque =
0.5 N.m (4.5 lb-in) (tighten using screwdriver diam. 3.5 mm)
Earthing
Protection rating
Overvoltage category
Pollution
Max operating Altitude
Mechanical resistance
Resistance to electrostatic discharge
Resistance to HF interference
Conducted and radiated emissions
Operating temperature
Storage temperature
Relative humidity
Mounting
Screw terminals connection capacity
Processing characteristics of CB, CD, XD & XB product
types
LCD display
Programming method
Program size
CD, XD : Display with 4 lines of 18 characters
Function blocks / SCF (Grafcet) or Ladder
For CB, CD :
4 Ko : 64 macros max.
256 blocks max. per macro
180 typical blocks
For XB, XD :
Unless otherwise specified, the characteristics given are applicable to all or part of the product range selected
02/11/2015
8 Ko : 64 macro max.
350 typical blocks
Or for CB, CD, XB, XD : 120 lines in Ladder
Flash EEPROM
EEPROM
368 bit/200 words
Program and settings in the controller : 10 years
Program and settings in the plug-in memory : 10 years
Data memory : 10 years
Function blocks : 6 →90 ms (typically 20 ms)
Ladder : typically 20 ms
Input acquisition time : 1 to 2 cycle times
10 years (lithium battery) at 25 °C
Drift < 12 min/year (at 25 °C)
6 s/month (at 25 °C with user-definable correction of drift)
1 % ± 2 cycle times
< 1,2 s
www.crouzet.com
Program memory
Removable memory
Data memory
Back-up time in the event of power failure
Cycle time
Response time
Clock data retention
Clock drift
Timer block accuracy
Start up time on power up
Characteristics of products with AC power supplied
Supply
Nominal voltage
Operating limits
Supply frequency range
Immunity from micro power cuts
Max. absorbed power
24 V AC
(88970..4)
24 V AC
-15 % / +20 %
or 20.4 VAC→28.8 VAC
50/60 Hz (+4 % / -6 %)
or 47→53 Hz/57 < 63 Hz
10 ms (repetition 20 times)
CB12-CD12-XD10-XB10 : 4 VA
CB20-CD20 : 6 VA
XD10-XB10 with extension : 7,5 VA
XD26-XB26 : 7.5 VA
XD26-XB26 with extension : 10 VA
1780 V AC
100 →240 V AC
(88970..3)
100 →240 V AC
-15 % / +10 %
or 85 VAC→264 VAC
50/60 Hz (+4 % / -6 %) or 47 →53 Hz/57 < 63 Hz
CB12-CD12-XD10-XB10 : 7 VA
CB20-CD20 : 11 VA
XD10-XB10 with extension : 12 VA
XD26-XB26 : 12 VA
XD26-XB26 with extension : 17 VA
1780 V AC
100 →240 V AC
(88970..3)
100 →240 V AC (-15
% / +10 %)
0,24 mA @ 85 V AC
0,75 mA @ 264 V AC
350 kΩ
≥ 79 V AC
>0.17 mA
≤ 20 V AC (≤ 28 V AC : XE10, XR06, XR10, XR14)
<0.5 mA
50 ms
State 0 < 1 (50/60 Hz)
Configurable in increments of 10 ms
50 ms min. up to 255 ms
State 0 →1 (50/60 Hz)
In accordance with cycle time (Tc) and input response time (Tr) :
1/ ( (2 x Tc) + Tr)
Contact or 3-wire PNP
Resistive
None
None
Yes
On LCD screen for CD and XD
Isolation voltage
Inputs
Input voltage
Input current
Input impedance
Logic 1 voltage threshold
Making current at logic state 1
Logic 0 voltage threshold
Release current at logic state 0
Response time with LADDER programming
Response time with function blocks programming
Maximum counting frequency
Sensor type
Input type
Isolation between power supply and inputs
Isolation between inputs
Protection against polarity inversions
Status indicator
24 V AC
(88970..4)
24 V AC (-15 % / +20 %)
4,4 mA @ 20,4 V AC
5,2 mA @ 24,0 V AC
6,3 mA @ 28,8 V AC
4.6 kΩ
≥ 14 V AC
>2 mA
≤ 5 V AC
<0.5 mA
50 ms
1/ ( (2 x Tc) + Tr)
Resistive
None
None
Yes
Characteristics of relay outputs common to the entire range
Max. breaking voltage
Breaking current
5 →30 V DC
24 →250 V AC
CB-CD-XB10-XD10-XR06-XR10 : 8 A
XD26-XB26 : 8 x 8 A relays, 2 x 5 A relays
XE10 : 4 x 5 A relays
XR14 : 4 x 8 A relays, 2 x 5 A relays
Usage category DC-12 : 24 V, 1.5 A
Usage category DC-13 : 24 V (L/R = 10 ms), 0.6 A
Usage category AC-12 : 230 V, 1.5 A
Usage category AC-15 : 230 V, 0.9 A
12A for O8,O9,OA
10 mA (at minimum voltage of 12 V)
12 V, 10 mA
Off load : 10 Hz
At operating current : 0.1 Hz
10,000,000 operations (cycles)
In accordance with IEC/EN 60947-1 and IEC/EN 60664-1 : 4 kV
Make 10 ms
Release 5 ms
Against short-circuits : None
Against overvoltages and overloads : None
Electrical durability for 500 000 operating cycles
Max. Output Common Current
Minimum switching capacity
Minimum load
Maximum rate
Mechanical life
Voltage for withstanding shocks
Off-cycle response time
Built-in protections
Status indicator
Characteristics of product with DC power supplied
02/11/2015
Supply
Nominal voltage
Operating limits
Max. absorbed power
12 V DC
(88970..5 & 8970814 & 88970840)
12 V DC
-13 % / +20 %
or 10.4 V DC < 14.4 V DC (including ripple)
≤ 1 ms (repetition 20 times)
CB12 with solid state outputs : 1.5 W
CD12 : 1.5 W
CD20 : 2.5 W
XD26-XB26 : 3 W
XD26-XB26 with extension : 5 W
XD26 with solid state outputs : 2.5 W
Yes
www.crouzet.com
24 V DC
(88970..1 et 88970..2)
24 V DC
-20 % / +25 %
or 19.2 V DC < 30 V DC (including ripple)
CB12-CD12-CD20 with solid state outputs - XD10-XB10 with solid state outputs : 3 W
XD10-XB10 with relay outputs : 4 W
XD26-XB26 with solid state outputs : 5 W
CB20-CD20 with relay outputs : 6 W
XD26 with relay outputs : 6 W
XD10-XB10 with extension : 8 W
XD26-XB26 with extension : 10 W
Yes
24 V DC
(88970..1 and 88970..2)
24 V DC (-20 % / +25 %)
2,6 mA @ 19,2 V DC
3,2 mA @ 24 V DC
4,0 mA @ 30,0 VDC
7.4 kΩ
≥ 15 V DC
≥2.2 mA
≤ 5 V DC
<0.75 mA
1 →2 cycle times + 6 ms
I1 & I2 : FBD (Up to 6 k Hz) & Ladder (1 k Hz)
I3 to IA & IH to IY : in accordance with cycle time (Tc) and input
response time (Tr) : 1/ ( (2 x Tc) + Tr)
Type 1
Resistive
None
None
Yes
24 V DC
4 inputs IB →IE
6 inputs IB →IG
(0 →10 V) or (0 →V power supply)
12 kΩ
30 V DC max
29 mV
Common mode
10 bit at maximum input voltage
Controller cycle time
±5%
± 6.2 %
±2%
None
10 m maximum, with shielded cable (sensor not isolated)
Yes
2.2 kΩ/0.5 W (recommended)
10 kΩ max.
1,6 mA @ 19,2 VDC
2,0 mA @ 24,0 V DC
2,5 mA @ 30,0 VDC
12 kΩ
≥ 15 VDC
≥1.2 mA
≤ 5 V DC
≤0.5 mA
1 →2 cycle times
1/ ( (2 x Tc) + Tr)
Type 1
Resistive
None
None
Yes
Digital inputs (I1 to IA and IH to IY)
Input voltage
Input current
Input impedance
Response time
Sensor type
Conforming to IEC/EN 61131-2
Input type
Status indicator
Analogue or digital inputs (IB to IG)
CB12-CD12-XD10-XB10
CB20-CD20-XB26-XD26
Inputs used as analogue inputsonly in FBD
Measurement range
Input impedance
Input voltage
Value of LSB
Input type
Resolution
Conversion time
Accuracy at 25 °C
Accuracy at 55 °C
Repeat accuracy at 55 °C
Isolation between analogue channel and power supply
Cable length
Potentiometer control
Inputs used as digital inputs
Input voltage
Input current
12 V DC
(88970..5 & 88970814 & 88970840)
12 V DC (-13 % / +20 %)
3,9 mA @ 10,44 V DC
4,4 mA @ 12,0 V DC
5,3 mA @ 14,4 VDC
2.7 kΩ
≥ 7 V DC
≥2 mA
≤ 3 V DC
<0.9 mA
Type 1
Resistive
None
None
Yes
12 V DC
4 inputs IB →IE
6 inputs IB →IG
14 kΩ
14.4 V DC max
14 mV
Common mode
±5%
± 6.2 %
±2%
None
Yes
10 kΩ max.
0,7 mA @ 10,44 VDC
0,9 mA @ 12,0 VDC
1,0 mA @ 14,4VDC
14 kΩ
≥ 7 V DC
≥0.5 mA
≤ 3 V DC
≤0.2 mA
1 →2 cycle times
1/ ( (2 x Tc) + Tr)
Type 1
Resistive
None
None
Yes
Input impedance
Response time
Maximum counting frequency in FBD
Sensor type
Input type
Status indicator
range
5 →30 V DC
24 →250 V AC
12A (10A UL) for O8,O9,OA
02/11/2015
Breaking current
CB-CD-XD10-XB10-XR06-XR10 : 8 A
12 V, 10 mA
Off load : 10 Hz
Make 10 ms
Release 5 ms
12 V DC
(88970814 & 88970840)
CB12 : O4
XD26 : O4 →O7
* Only available with "FBD" programming language
10.4 →30 VDC
12-24 V DC
0.5 A
0,625 A
≤ 2 V for I = 0.5 A (at state 1)
Make ≤ 1 ms
Release ≤ 1 ms
1 Maximum on inductive load
Against overloads and short-circuits : Yes
Against overvoltages (*) : Yes
Against inversions of power supply : Yes
(*) In the absence of a volt-free contact between the output of the
logic controller and the load
1 mA
0,2 A / 12 V DC
0,1 A / 24 V DC
No
14.11 Hz
56.45 Hz
112.90 Hz
225.80 Hz
451.59 Hz
1806.37 Hz
0 →100 % (256 steps for CD, XD and 1024 for XA)
< 5 % (20 % →80 %) load at 10 mA
50 mA
20 m
< 10 % (20 % →80 %) load at 10 mA
24 V DC
(88970..2)
CD12-XD10-XB10 : O4
CD20-XD26-XB26 : O4 →O7
www.crouzet.com
Minimum load
Maximum rate
Mechanical life
Status indicator
Digital / PWM solid state output
PWM solid state output*
Breaking voltage
Nominal voltage
Nominal current
Max. breaking current
Voltage drop
Response time
Operating frequency
Min. load
Maximum incandescent load
Galvanic isolation
PWM frequency
19.2 →30 VDC
24 V DC
0.5 A
0,625 A
Make ≤ 1 ms
Release ≤ 1 ms
1 mA
0,1 A / 24 V DC
No
14.11 Hz
56.45 Hz
112.90 Hz
225.80 Hz
451.59 Hz
1806.37 Hz
50 mA
20 m
PWM cyclic ratio
PWM accuracy at 120 Hz
Max. Breaking current PWM
Max. cable length PWM
PWM accuracy at 500 Hz
Status indicator
Accessories
M3 Soft
PA
PA
PA
PA
Multilingual programming software containing specific library functions (CD-ROM)
EEPROM memory cartridge
3 m serial link cable : PC →Millenium 3
USB cable 3 m : PC →Millenium 3
Millenium 3 interface →Bluetooth®
(class A 10 m)
88970111
88970108
88970102
88970109
88970104
Comments
* to be marketed 1
st
quarter 2006
Dimensions (mm)
XD26
02/11/2015
www.crouzet.com