LEGION ELECTRONIC
HARDWARE CO., LTD.
ROTARY SWITCH TEST SPECIFICATION
MODEL NO. MFR01 SERIES
1. Application temperature range (
2. Test condition (
: 5 ~ 35
: 45 ~ 85%
0~125
The switch is tested at a temperature range of 5~35 c and relative humidity range of 45~85%.
3. Rating (
8A 125/250VAC
FOR UL/C-UL
12A-8(3)A 250V~ μT125/55
for EUROPEAN SAFETY (ENEC)
4. Electric performance (
4-1.
Contact resistance
Measured by fall-of-potential method at dc 0.2v/1a should be less
than 50mΩ initial.
DC 0.2V/1A
50mΩ
4-2.
Insulation resistance (
Measured with dc 500v applied between terminals of open contacts and between terminal of
opposite polarity or metal part, should be more than 100MΩ.
DC 500V
100MΩ.
4-3.
Dielectric strength (
The switch shall withstand without breakdown a potential of ac 1500v 0.5mA for 1 minute
between terminals of open contacts and terminals of opposite polarity or metal part.
0.5mA 1500VAC
0.5mA 1500VAC
5. Overload and endurance test
UL & CSA STANDARD (
RATING: 8A 125/250VAC
MFR01
(SPEC-006)_1
CONDITION
VOLTAGE CURRENT
P.F.
OPERATION
SPEED
8 CYCLES PER
NUMBER OF
OPERATION
CYCLES
CYCLES
6000
SAFETY
APPLICATION
OVERLOAD
125VAC
12A
250VAC
0.75~0.8
MINUTE
8 CYCLES PER
UL/C-UL
(UL1054)
ENDURANCE
125VAC
8A
250VAC
0.75~0.8
MINUTE
UL/C-UL
(UL1054)
EUROPE STANDARD (
RATING: 12A-8(3)A 250V~ μT125/55
INCREASED VOLTAGE TEST AT ACCELERATED SPEED (
CONDITION
VOLTAGE CURRENT
P.F.
OPERATION
SPEED
NUMBER OF
OPERATION
SAFETY
APPLICATION
MAKING
287.5VAC
18A
0.6
15 CYCLES
PER
MINUTE
CYCLES
ENEC
(IEC61058)
BREAKING
12A
0.95
TEST AT LOW SPEED (
MAKING
BREAKING
250VAC
18A
12A
0.6
0.95
15 CYCLES
PER
MINUTE
CYCLES
ENEC
(IEC61058)
MAKING
BREAKING
250VAC
12A
18A
0.6
0.95
15 CYCLES
PER
MINUTE
CYCLES
9800
ENEC
(IEC61058)
6.
Temperature test
The temperature test should be taken after endurance test with its rated current and voltage.
The temperature rising shall not be more than 55 c.
MFR01
(SPEC-006)_1